Hi, I just received my labjack equipment yesterday, and I've already run into problems. I'm a newbie with programming, so I guess it's a simple question. I thought I could control my solid state relays (3-32VDC) with my digital outputs on my U3LV. But when i measure the voltage with the relay connected it only shows 2.0V. Am I doing something wrong or is it simply not possible? best regards, moeller

#2 LabJack Support

LabJack Support
  • Admin
  • 8677 posts

Posted 22 January 2013 - 07:49 AM

You can usually control SSRs with the digital I/O. Are you following the details here:

http://labjack.com/s...s-guide/2.8.1.4

Make sure you are connecting in the sinking configuration, and changing the line between output-low (SSR on) and input (SSR off).

When you measure 2.0 volts, is that across the +/- inputs of the SSR, or perhaps from some point versus GND? Which of the 3 states (input, output-high, output-low) is the digital I/O set to?

What is the control input resistance of your SSR?

#3 moeller

moeller
  • Members
  • 8 posts

Posted 22 January 2013 - 08:18 AM

thank you for your reply. I found the answer though the link. I mistake was that I had connected the DO to GND instead of VS.

#4 moeller

moeller
  • Members
  • 8 posts

Posted 22 January 2013 - 09:33 AM

You can usually control SSRs with the digital I/O. Are you following the details here:

http://labjack.com/s...s-guide/2.8.1.4

Make sure you are connecting in the sinking configuration, and changing the line between output-low (SSR on) and input (SSR off).

When you measure 2.0 volts, is that across the +/- inputs of the SSR, or perhaps from some point versus GND? Which of the 3 states (input, output-high, output-low) is the digital I/O set to?

What is the control input resistance of your SSR?


Ups, I was too fast. The SSR is still not working. If I follow the instructions from the link and uses DI and DO-low I get the voltage of 1,2V(DI) and 2,64V(DO-low). this is measured on the SSR +/- inputs. The SSR needs an input from 3-32VDC.

In the description it says that I should measure 3,7V.

Any suggestions?

#5 LabJack Support

LabJack Support
  • Admin
  • 8677 posts

Posted 22 January 2013 - 12:59 PM

What SSR are you using? Please provide a link to electrical specs for the SSR. Are using an FIO or EIO/CIO? Measuring 1.2V across the SSR control inputs when the line is set to input does not make sense for any SSR. Confirm this by measuring +control to GND (should be 5V) and -control to GND (should be 3.8V if you are dropping 1.2V across the SSR).

#6 moeller

moeller
  • Members
  • 8 posts

Posted 23 January 2013 - 09:15 AM

What SSR are you using? Please provide a link to electrical specs for the SSR.

Are using an FIO or EIO/CIO?

Measuring 1.2V across the SSR control inputs when the line is set to input does not make sense for any SSR. Confirm this by measuring +control to GND (should be 5V) and -control to GND (should be 3.8V if you are dropping 1.2V across the SSR).


I don't have any electrical specs on the relay, but I have attached a picture of it.

I am using FIO4.

When I set the line to input the voltage from +control to GND is 5V and from -control to GND 3,8V.

Attached Thumbnails

  • foto.JPG


#7 LabJack Support

LabJack Support
  • Admin
  • 8677 posts

Posted 23 January 2013 - 10:34 AM

Without more specs about the input circuit we can only guess what might be going on. To just try to get it working, I suggest you try using an EIO or CIO line, rather than an FIO, as they have lower source resistance. The other thing you can try is using a DAC line. Use a sourcing connection to connect DAC0 to +control and GND to -control. Set DAC0 to 5.0V to turn the SSR on and 0.0V to turn the SSR off.

#8 moeller

moeller
  • Members
  • 8 posts

Posted 23 January 2013 - 11:43 AM

Without more specs about the input circuit we can only guess what might be going on. To just try to get it working, I suggest you try using an EIO or CIO line, rather than an FIO, as they have lower source resistance.

The other thing you can try is using a DAC line. Use a sourcing connection to connect DAC0 to +control and GND to -control. Set DAC0 to 5.0V to turn the SSR on and 0.0V to turn the SSR off.



I works fine when I'm using the DAC line, but I need to control more than to SSR and the U3 only have 2 DAC lines.

I will try using an EIO or CIO line tomorrow to see if that fixes the problem.

The relays is suppose to switch off a 100W heating element than uses 230V.

best regards,

Moeller

#9 LabJack Support

LabJack Support
  • Admin
  • 8677 posts

Posted 23 January 2013 - 01:38 PM

Other solutions are to use a different SSR (we often recommend the Jameco 176719 for 24-280 VAC) or to use the LJTick-RelayDriver to drive your CKELE relay:

http://labjack.com/s...river/datasheet